Lead/Lag Problems on Stulz Units

Lead–Lag Not Rotating — Quick Check (STULZ E²)

Goal: find why the Lead isn’t handing over to Standby/Assist and restore normal rotation/failover.

 

60-Second Screen Checks (on any unit)

 

Service → Group → Group Status

  •  All expected units show Online (no “No Link”).

  •  Current Lead unit is identified.

  •  Active / Assist / Standby counts look right.

 

Service → Group → Group Rotation

  •  Rotation is Enabled.

  •  Rotate Every (hrs/days/weeks) > 0 and sensible.

  •  Next Rotation time looks reasonable (clock not wrong).

  •  Force Rotation is available (not greyed).

 

Service → Group → Group Config

  •  Unit is Included in Group and Included in Rotation (not excluded).

  •  Min Active / Min Assist aren’t blocking a changeover.

  •  No unit is Inhibited / Manual / Locked Lead.

 

Service → Group → Group Alarm Setup

  •  Alarms that should trigger changeover are enabled.

  •  No active alarm is pinning the group in a protective state.

 

Date/Time (System)

  •  Controller clock/time-zone is correct (rotation schedules depend on it).

 

Service → Group → Group Sensors / Averaging

  •  Sensor source (Local/Lead/Average/Min/Max) matches your strategy.

  •  Standby/Assist sensors included/excluded as intended (avoids “false no-demand”).

 

5-Minute Network/Setup Checks

 

pLAN addressing (E²)

  •  Controllers addressed 1..8 with no gaps.

  •  Terminal↔Controller pairs follow the sum-to-33 rule (32↔1, 31↔2 …).

  •  Net/Bus status shows all controllers/terminals healthy.

 

Configuration consistency

  •  All units share the same setpoint/deadband/modes (no “fighting” logic).

  •  Same assist cut-in/out logic and humidity strategy.

  •  No unit held Off by BMS/remote interlock.

 

Comms wiring

  •  Correct polarity, good shields, proper termination at both ends only.

  •  No stubs or crushed cables at doors/panels.

 

Safe Force-Rotation Test (proves the path)

  1. Ensure both units are Online and no critical alarms.

  2. Temporarily set Min Active = 1 (so a changeover is allowed).

  3. Service → Group → Group Rotation → Force Rotation.

  4. Confirm Lead flips to the next addressed unit and the prior lead drops to Standby/Assist.

  5. Restore Min Active and any temporary changes.

 

If Force Rotation fails: almost always addressing/group membership or rotation disabled (re-check the two sections above).

Usual Culprits & Fixes


  • Rotation disabled / value = 0 → Enable and set a real interval.

  • Bad clock → Correct date/time; recheck “Next Rotation”.

  • Min Active too high → Lower so a handover is legal.

  • Unit excluded / inhibited / manual → Re-include and clear inhibit/manual.

  • Active alarm holding state → Clear alarm or change Group Alarm Setup logic.

  • Addresses skipped (e.g., 1 & 3 only) → Make them contiguous; rotation follows address order.

  • Terminal not paired to the right controller → Fix pairing (sum-to-33 rule).

  • BMS holding lead on (remote enable/global mode) → Release override; test again.

  • Mismatched setpoints/deadbands → Align; otherwise the group may never meet the condition to rotate.

 

Quick notes (older A-Tech-20 sites)

  • Level-3 password often 9998 (may be site-changed).

  • Communications → Unit Number must be 001, 002, 003… (no skips).

  • Match baud/parity on every unit/gateway.

 

Handy one-liner for the job sheet


Fix rule: If rotation is enabled, the clock is correct, addresses are contiguous, Min Active allows a swap, units are included & healthy, and Force Rotation works—lead-lag will rotate on schedule.