Cooling Tower Shutdown procedure

Emergency Cooling Tower Shutdown – SOP
Purpose: Safe, compliant shutdown of cooling towers during emergencies (Legionella, equipment failure, or hazards).
1. Triggers
Legionella detected above limits
Major leaks, pump/fan/electrical failure
Unsafe access or structural hazard
Loss of chemical dosing or monitoring
Direction from SA Health, SafeWork SA or Local Council
2. Roles
Supervisor: Authorise, notify, log event
Maintenance: Perform shutdown, isolate systems
Safety Officer: Ensure WHS compliance
Water Treatment Contractor: Assist with chemical isolation/disinfection
3. Required PPE
Gloves, goggles, chemical suit, harness (if height work), LOTO kit, communication device.
Emergency Cooling Tower Shutdown – Key Steps
1. Notify & Log
Alert the control room, maintenance team, safety officer, and water treatment contractor immediately.
Record the incident in the site log for traceability.
2. Isolate Systems
Shut down fans, pumps, and chemical dosing equipment.
Apply lockout/tagout (LOTO) to all electrical supplies, chemical lines, and make-up valves.
3. Drain & Contain
Drain basins and pipework to a safe, approved outlet.
Use spill kits to contain and clean any chemical or water discharge.
4. Secure the Area
Display “Offline – DO NOT OPERATE” signage.
Restrict access to the cooling tower to authorised personnel only.
5. Report
Document time, cause, actions taken, and personnel involved.
If Legionella is involved, notify SA Health, local council and SafeWork (workplace health and safety regulator) within 24 hours.
6. Prepare for Restart
Complete a full inspection, cleaning, and disinfection of the system.
Confirm clearance from the safety officer and water treatment contractor before bringing the tower back online.
5. Records
Shutdown log
Isolation tags
Incident report
Sampling results
References
SA Health Legionella Guidelines
SafeWork SA WHS Rules
Cooling Tower OEM manuals