How to test a single-phase capacitor start/run motor windings


Step 1 — Safety
Turn power OFF at isolator or breaker
Confirm the motor is not live
Step 2 — Identify the motor wires
Find the 3 motor terminals or wires:
C = Common
R = Run winding
S = Start winding
Step 3 — Disconnect the capacitor
Remove 1 capacitor wire from either side
This stops the capacitor from affecting your readings
Step 4 — Set your multimeter
Set to Ohms (Ω) mode
Step 5 — Test all 3 winding paths
C ↔ R → checks the run winding
C ↔ S → checks the start winding
R ↔ S → checks both windings in series
Healthy motor windings will show
A resistance number on all 3 tests
C↔R = lowest Ω → normal
C↔S = higher than run Ω → normal
R↔S = highest Ω → also normal when the capacitor is disconnected, because this is both windings in a loop
Important note
R ↔ S will always show the highest resistance when the capacitor is removed
This is correct and does not mean the windings are faulty
Check for shorts to ground
Test each wire (C, R, S) to the motor’s metal body
No reading / no beep = PASS
Beep or a number = FAIL (short to motor body)
Fault signs
OL (no reading) on C↔R or C↔S → broken winding → FAIL
0Ω or near 0Ω → shorted winding → FAIL
OL on R↔S only → capacitor circuit open (windings can still be OK)
Final result
If windings show resistance and nothing connects to the motor body → windings are healthy
If any winding test fails → motor needs repair or replacement