How to test a single-phase capacitor start/run motor windings

  • Step 1 — Safety

    • Turn power OFF at isolator or breaker

    • Confirm the motor is not live

 

  • Step 2 — Identify the motor wires

    • Find the 3 motor terminals or wires:

      • C = Common

      • R = Run winding

      • S = Start winding

 

  • Step 3 — Disconnect the capacitor

    • Remove 1 capacitor wire from either side

    • This stops the capacitor from affecting your readings

 

  • Step 4 — Set your multimeter

    • Set to Ohms (Ω) mode

 

  • Step 5 — Test all 3 winding paths

    • C ↔ R → checks the run winding

    • C ↔ S → checks the start winding

    • R ↔ S → checks both windings in series

 

  • Healthy motor windings will show

    • A resistance number on all 3 tests

    • C↔R = lowest Ω → normal

    • C↔S = higher than run Ω → normal

    • R↔S = highest Ω → also normal when the capacitor is disconnected, because this is both windings in a loop

 

  • Important note

    • R ↔ S will always show the highest resistance when the capacitor is removed

    • This is correct and does not mean the windings are faulty

 

  • Check for shorts to ground

    • Test each wire (C, R, S) to the motor’s metal body

    • No reading / no beep = PASS

    • Beep or a number = FAIL (short to motor body)

 

  • Fault signs

    • OL (no reading) on C↔R or C↔S → broken winding → FAIL

    • 0Ω or near 0Ω → shorted winding → FAIL

    • OL on R↔S only → capacitor circuit open (windings can still be OK)

 

  • Final result

    • If windings show resistance and nothing connects to the motor body → windings are healthy

    • If any winding test fails → motor needs repair or replacement

 

 